safety switch on oil furnace keeps going off

damon booz
damon booz Member Posts: 11
The furnace safety switch keeps going off from time to time (very sporadic -- approx. 1/day). We've talked to several professionals and they seem perplexed as well. We go down and push the safety and it starts right up. I do smell a bit of oil from time to time right when it starts up.

Comments

  • John Mills_3
    John Mills_3 Member Posts: 221
    HAVE

    any of these professionals looked at the furnace?
  • ed wallace
    ed wallace Member Posts: 1,613
    oil burner

    have the system cleaned and serviced quit pushing the reset button

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Jim Davis
    Jim Davis Member Posts: 305
    oil safety

    Anytime the oil safety locks out it is because the flame failed to light in the first 30-45 seconds. Many times this is do to loss of prime during extended off periods. But many other problems could cause the same situation such as a worn coupling, weak transformer, poorly positioned electrodes, bad oil burner motor. A combustion test that includes CO readings Start-Run-Shutdown is the only way to narrow the problem down. I have seen every part replace on an oil furnace and the problem continued.
  • damon booz
    damon booz Member Posts: 11


    yes, one fellow looked at it a couple times... replaced nozzles, oil filter, etc. ---it looks good for a week and then starts happening again.
  • damon booz
    damon booz Member Posts: 11


    a professional has serviced our boiler several times and to no avail---it always looks good for a couple days and then starts coming back again.
  • damon booz
    damon booz Member Posts: 11


    thanks for your very knowledgeable and thorough response. I have been thinking about this problem often and was puzzled. I have talked to a couple pro's and had a service man out a couple times and still could not solve the problem. I never considered the prime issue---is there any way to resolve a prime loss?
  • ed wallace
    ed wallace Member Posts: 1,613
    oil burner problem

    > thanks for your very knowledgeable and thorough

    > response. I have been thinking about this

    > problem often and was puzzled. I have talked to

    > a couple pro's and had a service man out a couple

    > times and still could not solve the problem. I

    > never considered the prime issue---is there any

    > way to resolve a prime loss?



    ask your oil man if he has an onwatch oil monitoring system and if he does have hij hook it up to the oil burner it will monitor the burner for problems

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Mark Wolff
    Mark Wolff Member Posts: 256
    Resolve a prime loss

    Have the service guy check every fitting in your fuel supply line. If they were all tight and you have lost prime

    A. Replace the fuel lines from the tank to the boiler.
    B. Install a Tigerloop Oil Deaerator (it removes air from the line and provides a small day tank of fuel by the boiler. Additionally the flow check valve should compensate for a possible weak check in the pump.


    Before that though, have the service technician push the reset and right after the furnace fires cross the FF terminals on the primary control (this tells the furnace that there is still a flame). If the primary control still trips out check the other items. If it keeps running, replace the cadmium eye.
  • steve_29
    steve_29 Member Posts: 185


    Is your tank located outside or in a cold enviroment? What are you using for fuel?
  • damon booz
    damon booz Member Posts: 11


    Thanks,
    I'm going to replace the fuel line.
  • damon booz
    damon booz Member Posts: 11


    The tanks are inside and we use oil.

  • jim lockard
    jim lockard Member Posts: 1,059
    fittings

    Fitting for the oil line(s) are they flare or compression ?
    All of your fittings must be flare if not change em. Best Wishes J.Lockard
  • CDFishies
    CDFishies Member Posts: 1
    Same thing...

    happened to me last year. First they thought it was sludge from the tank, then it was the sight inside the gun, then they thought the shut-off was leaking. In the end, I replaced the old gun with a rebuilt one and the problem went away. This summer I replaced the entire system with a gas boiler and I'm lovin it!
  • ed wallace
    ed wallace Member Posts: 1,613
    oil reset

    if the unit locksout in the middle of the night it could be a weak transformer or a bad air adjustment

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • JacktheShack
    JacktheShack Member Posts: 9
    Intermittent Safety Lockout

    > if the unit locksout in the middle of the night

    > it could be a weak transformer or a bad air

    > adjustment

    >

    > _A

    > HREF="http://www.heatinghelp.com/getListed.cfm?id=

    > 256&Step=30"_To Learn More About This

    > Professional, Click Here to Visit Their Ad in

    > "Find A Contractor"_/A_



    > if the unit locksout in the middle of the night

    > it could be a weak transformer or a bad air

    > adjustment

    >

    > _A

    > HREF="http://www.heatinghelp.com/getListed.cfm?id=

    > 256&Step=30"_To Learn More About This

    > Professional, Click Here to Visit Their Ad in

    > "Find A Contractor"_/A_



    What make of burner do you have & does it have an oil-delay valve??

    I've had this same thing happen to my Beckett AFG oil burner; it turned out to be an intermittent failure of the solenoid oil delay valve which sits on top of the fuel pump; to test the valve, it can be completely removed from the pump to see if this clears up the problem.
  • damon booz
    damon booz Member Posts: 11


    You, my friend, hit the nail on the head. Yesterday, I stayed home from work to figure out this problem once and for all. I had my friend, who repairs oil burners for a living, come out and double-check my diagnosis. I was going through alot of the responses on "The Wall" and narrowing down the problem...the transformer spark seemed weak(about 1/4"), which made sense. So, while I was writing down the model# off of the transformer, I heard a grinding noise in the motor right before the furnace started up and it soon went off on safety. To make a long story short, my friend and I replaced the burner motor, and the transformer and she's been purring like a kitten ever since. Thanks again to everybody for their invaluable help.
  • damon booz
    damon booz Member Posts: 11


    Excellent point! Although I resolved the immediate problem with the safety popping up (which was happening 3/day) by changing the transformer and gun motor yesterday, only time will tell if I will get my normal "off on safety once/week" problem back. I was wondering myself about that solenoid oil-delay valve (by the way, mine is also a Beckett AFG gun) wondering if that might be the culprit for my intermittent problem. It's nice to hear that you solved yours by replacing that valve, and if my intermittent problem crops up again, I will surely suspect this valve. HOw would I go about testing this? Thanks greatly for all of your help.
  • JacktheShack
    JacktheShack Member Posts: 9
    Checking Delay Valve

    The delay valve solenoid can be checked by changing the upper coil section with a new one ($5-$10) by unplugging the 120v connector & removing the 3/8" nut; the coil slips right off & the new one is slipped on; the other way is to remove the valve from the pump & connect the connector tube to the pump nozzle port (the original fitting on the older suntec pumps is needed); the burner will run fine without the delay valve while you watch it for a few days to see if that is the problem.
  • JacktheShack
    JacktheShack Member Posts: 9
    Checking Delay Valve

    The delay valve solenoid can be checked by exchanging only the upper coil section with a new one ($5-$10) by unplugging the 120v connector & removing the 3/8" nut; the upper coil slips right off & the new one is slipped on; the other way is to remove the valve from the pump & connect the connector tube to the pump nozzle port (the original fitting on the older suntec pumps is needed); the burner will run fine without the delay valve while you watch it for a few days to see if that is the problem.
  • JacktheShack
    JacktheShack Member Posts: 9
    Checking Delay Valve

    The delay valve solenoid can be checked by exchanging only the upper coil section with a new one ($5-$10) by unplugging the 120v connector & removing the 3/8" nut; the upper coil slips right off & the new one is slipped on; the other way is to remove the valve from the pump & connect the connector tube to the pump nozzle port (the original fitting on the older suntec pumps is needed); the burner will run fine without the delay valve while you watch it for a few days to see if that is the problem.