Burnham steam boiler w/ two tappings, appears to be set up correctly, but:
When making steam, water level rises substantially (2 - 3 inches above "off" level) and right after shut off for high pressure, level drops substantially ( to 2 - 3 inches below "off" level; yup, that's 4 to 6 inches total ). As a result, I think the boiler is getting overfilled, and at it's peak the water goes up to the top of the glass, and I'm getting wet steam.
It almost seems as if there's some vacuum being created after the burner kicks out at high pressure, and the water is being "sucked" out of the boiler.
Any ideas?
  • Vito_3
    Vito_3 Member Posts: 1
    LEAKY STEAM VENT
    One of my steam radiators is leaking a lot of water after a long heating cycle. In fact if I remove the vent a great deal of water is ejected under pressure. I have had a great deal of problems with this radiator before. Any ideas?
    Steamhead Member Posts: 17,503
    That sounds like a dirty water problem
    Try flushing and skimming the boiler. Dirty water, or oil sitting on top of the water, will interfere with proper steaming and cause zooming water levels. This is really a job for a pro- you can locate one on the Find a Professional page of this site.
    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
    Consulting
    First thing to check
    is whether the steam supply valve (and the valve on the return if this is a 2-pipe air-vent system) is all the way open. If not, open it all the way. Then check to see if the radiator is off-level. It should be level, or pitched slightly toward the steam connection if it's a one-pipe radiator.
    Consulting
  • marty_4
    re: dirty water problem
    That was my first thought, but the boiler was skimmed and then chemically treated. Same problem.
    \"Chemically treated\"
    might just be the problem. Sometimes chemicals make the situation worse. Or, more dirt could have washed into the boiler from out in the system. Did the contractor flush out the return lines?
    Consulting
  • marty_4
    return lines
    As far as I know, they didn't flush the returns, but I'm not sure. (I'm also not sure what/how you flush the retuns; are we talking about the returns for the whole system? (as opposed to "near boiler piping" only?)).
    PS another contractor thought it was that the header was undersized, but that doesn't make sense to me. Could that be it?
    Flushing returns
    we're talking about "wet" returns here, those that run below the boiler's water line. I like to hook up a hose to the main vent opening and let the water run down the drip line, thru the return and out.
    Burnham's web site has installation manuals on it, these include piping diagrams. Download a copy to compare the diagarm to what was installed.
    www.burnham.com
    Consulting
  • marty_4
    wet returns
    Just so you know, there's about 200 feet of wet returns.
  • chuck_6
    chuck_6 Member Posts: 107
    How often to clean dirty water
    Steamhead: