pressurtrol settings incorrect?
S. Meredith
Member Posts: 5
After reading the Got Steam Heat book for Homeowners, I did a little exploring around the system. I have one pipe steam with a coal converted boiler (the house is c. 1850). The pressurtrol cut-in is set to 2, and the diff is set to 1. What does this do to my system? The book says .5 for cut-in. The heating is fair, needs a little cleaning, may
0
Comments
-
It should be set as low as it will go
Those systems were designed to heat the house on the coldest day of the year with no more than 2 pounds pressure. Anything more wastes fuel.
If the system is only "fair" in the way it heats, you would do well to have a good steam man look it over. Often it can be made to run better for much less than you'd spend on a new boiler. Try the Find a Professional page of this site to locate one near you.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Would the current setting cause any serious damage or noticeably annoying problems? Will I notice a change in my system when I change the cut-in to .5? Just curious.0 -
honeywell PA404 pressuretrol
I a singlepipe steam system with a gas fired boiler. The boiler is a weil macclain and is 19 years old. This system has two pressuretrols mounted on it. One has cutin set to .5 with the differential switch set to 1 The other has cut in set to 2 and differential set to 1 . I have never seen this type of setup. I was thinking that the two controls should be set to the same settings? any ideas?0 -
Dave is it a Powerpile system?
If it is then the second pressuretrol is designed to shut the pilot system off in the event of a run away boiler. That auxillary pressuretrol should be set for 14 lbs off 9 lbs on. Set the cut in to 9 and differential to 5. Make sure it is the one wired into the pilot generator circuit not the thermostat circuit.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements