Can I remove all the cast iron convectors on a system and install copper fin-tube? Do I size fin-tube for load or do I need to worry about piping resistance? My plan is to supply and return the BB with the tees that are in place. Will it work?
0
Comments
-
Why?
Why would you want to do this?0 -
?s
Cast iron tubular radiators, or cast iron baseboards?
You would be ill-advised to swap cast iron baseboards for fin-tube.
But if you are look to get rid of cast iron baseboards, I know where you can get rid of them, cheap. ;-)0 -
someone
turned the thermostat off in the house and it was not check for over a week. Outside temps were -10 to -15. Froze and cracked all 16 A/S Sunrad convectors. I'm doing it because I have to, not because I want to. Will the BB work?0 -
Is this a rental property?
0 -
unoccupied
Catholic Rectory. No full time priest, obviously no one checked on it through the holidays.0 -
It will work if sized correctly
and if the Monoflo tees will divert enough water to feed the baseboards. You may run into trouble here because the usual fin-tube baseboard needs higher flow rates than cast-iron radiators do.
Several companies make cast-iron baseboard- this might be the way to go.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
in Midwest
finding new cast iron BB maybe tough to do. Thank you for the suggestion, I was not sure if we could get water through the BB or not. Do you know if there is a way to tell what the pressure drop through the tee or the rad needs to be? Will try to track down Cast BB in the Morning.0 -
Maybe not so hard
Any Burnham, Slant/Fin or Weil-McLain dealer should be able to get it for you.
Get a copy of Dan's book "E.D.R.". It has rating charts for many old radiators and I believe your Sunrads are in it. Then you'll know how much heat each radiator is supposed to get. If the building has had insulation, storm windows etc. added, do a heat-loss on each room and size your new units from this. You might be able to use smaller units, or run with a lower water temperature.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
ratings
I have an American Standard ratings book that gives me the ratings for each section/radiator. I just replaced the boiler this fall with a Munchkin. Low temps are a good thing, but am concerned with water flow.0 -
But no low temp with fin-tube. Fin-tibe likes higher temps than Cast iron. You may end up with losts more baseboard. Than old Rads.
Where in the mid-west are you.
Mike0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements