Radiant, Hot-water heaters, & Pennsylvania
Jamie_6
Member Posts: 710
I have a small radiant job that requires 7,000 Btu's of 140 degree water for a Wirsbo Quick Trac job. I would like to use a 40 gallon hot-water heater with a flat plate heat ex-changer for the radiant side and a mixing valve for domestic use. I would like to know
1.Is this possible?
2. Has anyone done it?
3. Is it ASME compliant to do it this way?
Thanks agian,
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
1.Is this possible?
2. Has anyone done it?
3. Is it ASME compliant to do it this way?
Thanks agian,
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Danfoss has
a nice HX package for that purpose.
You may not get to 140 on the B side however. Lots of water heaters these days won't go past 140 on their aquastat. With the loss through the HX you might not get the output needed.
Liability issues, I suppose.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
been there done that
Yes, that can be done & we've installed several potable/hydronic systems utilizing a FP HX.
If you size your BB for 130 F, you'll be on target.
If the tank is an ASME model, that should cover your bases. There's a new PA boiler inspector serving our area, so it's once again a new ball game and another adjustment until we learn what particular items he deems important. If you have any doubts, I'd call them and ask for a determination in advance.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements