Radiant, Hot-water heaters, & Pennsylvania
Options
Jamie_6
Member Posts: 710
I have a small radiant job that requires 7,000 Btu's of 140 degree water for a Wirsbo Quick Trac job. I would like to use a 40 gallon hot-water heater with a flat plate heat ex-changer for the radiant side and a mixing valve for domestic use. I would like to know
1.Is this possible?
2. Has anyone done it?
3. Is it ASME compliant to do it this way?
Thanks agian,
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
1.Is this possible?
2. Has anyone done it?
3. Is it ASME compliant to do it this way?
Thanks agian,
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Danfoss has
a nice HX package for that purpose.
You may not get to 140 on the B side however. Lots of water heaters these days won't go past 140 on their aquastat. With the loss through the HX you might not get the output needed.
Liability issues, I suppose.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
been there done that
Yes, that can be done & we've installed several potable/hydronic systems utilizing a FP HX.
If you size your BB for 130 F, you'll be on target.
If the tank is an ASME model, that should cover your bases. There's a new PA boiler inspector serving our area, so it's once again a new ball game and another adjustment until we learn what particular items he deems important. If you have any doubts, I'd call them and ask for a determination in advance.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements