How would you pipe and control this?
Boiler connected to - baseboard zone, pool heat exchanger, & slab around the pool/changing area. Any ideas? I'm thinking pri/sec for piping. T-stat controls circ for bb zone; sensor on pool water return control circ for pool ht xchanger; and slab sensor controls circ for radiant(simple mixing valve for the slab). I could then use a tekmar 256 to reset boiler water based on outdoor temp. When any zone calls primary circ would run plus boiler if needed. Your ideas will be appreciated.
Thanks Pat
  • hr
    hr Posts: 6,106
    Got enough
    horsepower for all that? Swimming pools can consume large quantities of BTU's per hour :)
    Unless you are using a condensing boiler, make sure you have adequate return temperature protection.
    How will you handle a call from the baseboard zone only. Seems you boiler may be grossly oversized for a call from that zone only.
    Would a seperate pool heater, for just the pool, be a better option?
    hot rod
    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"