Bleeding Hydronic System

KeithP
KeithP Member Posts: 1
I have a hydronic system with 4 loops, 2 downstairs, 2 up. 1 of the upstairs loops was not heating. I turned off the other zone valves and it then heated up.
I have now left the affected zone fully open and the others 50% open.
What could cause this?

Also the rads (baseboard) have 'automatic ' bleeders, with a tire type valve on the top, should these be pressurised or just left alone.

Apart from this its a brilliant system.

Comments

  • Dan Peel
    Dan Peel Member Posts: 431
    new system or new problem?

    The source of your trouble could be a piping error, circulator placement problem, air issues, bypass piping or a variety of similar causes. Best guess without seeing would be the circulator is too small, installed on the return and relying on balance across the 4 zone valves to induce flow. Your current solution of restricting flow for the 3 zones should enable the 4th zone to receive more of the flow. This may mask the problem but will not fix it. Enjoy....Dan

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"