pre and post purge
Live/Learn
Member Posts: 97
Hi! A question from a home owner diy . I recently installed a burnham v83 to replace an old weil that was 45 years old, My new boiler has a beckett burner with a pre and post purge feature. When ever the burner comes on it comes on with a "bang" sometimes more than at other times. I expect some noise as I realize that the pump is going from almost no pressure to 180psi all at once. My question is is this harmful to the boiler? I have noticed what appears to be small hairline cracks in the target wall when viewed from the inspection port. By the way a tech from Petro came by and set it up with instruments. Thanks learn /Live
0
Comments
-
I believe......
....that an improper "Z-dimension" setting will cause a noisy startup on these burners. My experience has been that you need to physically check the Z setting, rather than rely on the little sticker that shows the proper position of the electrode assembly. I think you need to reference the actual Beckett manual for this burner, as the Burnham manual does not specify the Z setting for a burner with an L head on it. Last V83 I installed came with the Beckett manual along with the Burnham manual.
Hope this helps.
Starch0 -
Does this beast.....
Happen to have an outside air intake kit on it ? If it does, check Beckett for a nozzle line heater. Cold oil tends to light hard, and outside air will be flowing down that blast tube while the unit is off. This is definately NOT a diy project. It needs to be wired properly so it doesn't shut off during the off cycle! Chris0 -
new burnham
oil pressure is way to high needs to be changed you need a tech to do all the adjustments using a combustion test kit it cant be done by eye
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
pre and post purge
Hi again and thanks for your help so far. I'll give some more information to clearify my situation. I'm running a .75-45 degree solid nozzel @180psi as stated in my Burnham literature. I had it instrument tested by a Petro tech and the readings are as follows: draft: .02-.03; stack temp: 400 net; co2: 12. I do not have or require o/s air for combustion as the boiler area has adequate ventilation. I hope this helps, Thanks again.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements