Steam coils...HELP
Unknown
Member
CFM times Delta T (air, in °F) divided by 800.
That gives pounds per hour steam.
PPH= Sq Ft EDR divided by 4
Noel
That gives pounds per hour steam.
PPH= Sq Ft EDR divided by 4
Noel
0
Comments
-
Steam coils...HELP
Replacing a boiler that has two Flexitube coil set ups in old air handlers. Company that produced them was Aerofin in Newark. Date on tag 1925. Looks like each air handler has two coils on top of each other...I need the EDR to size the boiler. Looking in my every darn radiator book but no luck so far. They are 29" x 36" x 5". Any help asap would be much apprec iated.
Paul
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
OK Noel
Just a question on that. Believe it or not the company is still in business but i need to go measure the coils to get an idea of btu output. So in your deal lets use an example... 1500 cfm times 70 divided by 800=131.25
Then 131.25 times 4 coils= 525. 525 times 240 =126,000 Does this sound right? Now to get cfm on old belt drive I am going to measure the wheel and there you go I should get a cfm rating.
Paul
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Noel Question in above post
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Looks Ok to me
I'm going to go through it again, though, just in case.
Noel0 -
Noel heres the deal
I measured the blower wheel and looking in a Lau book on blowers the CFM is approx. 3000...Now I need 3000 x 70 = 210,000...210,000 divided by 800 equals...262.5
262.5 according to you is PPH. So I would then have to multiply that by 4 to get EDR. That would be 1050 sq ft EDR. Something is not right because the house is big but I have two units this size plus radiators and it would be a total edr of 2550...House isnt that big. I looked at the coils and they are not that big either.
Thanks Paul
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
CFM sounds high for the house
What size ducts are they? Is that the measured temp rise? Air isn't my strong suit, Anybody else here good with air?
Noel0 -
cfm
You say you looked in the Lau book for cfm, what is your blower rpm. Then check the lau book based on that rpm. Tim0 -
I know it sounds high
I am winging it based on the wheel size but it is 50+ years old. I am thinking that the cfm is more around 1200-1400 tops. Looking at hydronic coil air handlers we sell. Ducts are huge and old and the blower motor is only 1/3 hp. LLets say 30 degree temp rise?
Paul
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
New info
Spoke with the rep from the coil manufacturer. He figured cfm based on suface area. Now he says the coils can put out a min. of 196,000 btuh. Way too much heat for this house. I need to size the boiler correctly what do you guys suggest. they are copper coils...
Paul...............Should I be doing a heat load at this point and size to what the home needs and not the coil ratings?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
If......
If they take any raw outside air in, you ought not consider water. Steam has the advantage of being empty during boiler outages.
Otherwise.... Water to the coils and a heat loss survey to determine load demand, and partial reset to lengthen the cycle without blowing cold air.
How has it been working in the past? Did they like it? Sure has room for improvement....
Noel0 -
Fine I assume
No complaints for the most part. We are leaving the steam coils but I need to size the new boiler. 445.26 sqftEDR for cast iron in home. Need to figure what to add to that based on these coils or load of the house.
Paul
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
That's the issue
These, on steam, will chew through a lot of steam when they run. If you don't meet the demand, the shortage of steam might not be where you would like it. That's my fear of undersizing.
When they both run together, you'll see that demand.
Noel0 -
Cart Before The Horse
First, do a heat load calc (many programs available from suppliers etc or you can do it manually) pay particular attention to improvements in windows, insulation, etc. Very likely your heat load is less than it was originally.
Then ask what do the Air Handlers serve? Fresh air make up,
basic heat or what.
Then figure how many BTUs they need to acomplish the task. If it is make up air (doubtful unless it is a mansion) the Delta T is much greater (like 70) than for heat. Anyhow
BTU/Hr = CFM x Delta T x 1.08.
Again,if this is make-up air you would add this amount to your basic heat load. If it is just space heatng it would be part of your load & no addition is necesary.0 -
Good deal guys
Been on the phone with the manufacturer rep, on here with you guys, and my own research. The rep. came up with the final deal. Going to get the boiler. I will take some pics...I appreciate all the help, more than I can express on line. Owe you all a beer and a shot.
Iwill keep you posted.
Paul
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements