Tracer Wire for Radiant Heating?

John Ruhnke1
John Ruhnke1 Member Posts: 154
Has anybody tried this? I have a client that wants to install radiant into a comercial space but doesn't have a tennent yet. They are worried that when the tennent moves in they may want to attach things to the floor. I thought of using a tracer wire so you can use a metel detector to exactly pinpoint the pipes so as not to hit them.

JR

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=96&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • hr
    hr Member Posts: 6,106
    Actually Heatway

    used to offer a tube with a tracer wire for that purpose. Used to, being the catch phrase.

    I suppose you could lay your own wire, along with ther tube.

    Not sure if a detector could pick the wire from the rebar or remesh??

    I've taken digital pics or video with a 100 foot tape measure next to the tube for a "map"

    Also done "as built" drawing with the tube layout dimensioned.

    I'm not convinced the tube stays EXACTLY where it was placed when the concrete and workers get done with it :)

    You could probably be accurate within a couple inches.

    Keep the tube deep for jobs that will shot or use drop anchors that go 2" deep. Same issue with floaters also, how deep is the tube REALLY.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Kal Row
    Kal Row Member Posts: 1,520
    ouch

    radiant in a floor without a, floor finish, prelaid and lease gauranteed to be left alone, heaven help you
  • John Ruhnke1
    John Ruhnke1 Member Posts: 154
    Its what the client wants.............

    I only do what the client wants. Of course I warn them of the future problems, but if they feel those problems are solvable and want to go forward, why not? Wirsbo recommends installing radiant into the slab for future possible use. Many contractors have done it before.

    JR

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • What about PAP

    The aluminium barrier will show up on your metal detector. Of course if wire mesh or re-mesh is used like hr says, that won't work and only a good map will due.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • jw
    jw Member Posts: 62
    Kitec's XPA and a tracer works!

    I needed to find where my tubing was so a hoist could be bolted down to a slab. Luckily I had used kitec XPA with the aluminum. What I did was borrow the line finding equipment from the local gas utility, exposed the aluminum on the tube so I could connect the tracer to it, and then proceeded to use the finder and a can of paint to mark out the location of the loops! Could not have been sweeter.

    Even tho I take pix of the installs, I don't trust mr murphy, hence the linefinder.

    have fun!

    jw
  • S Davis
    S Davis Member Posts: 491


    I have used an infra red thermometer with good success.
    it's not perfect but you can tell pretty close where the tube is.

    S Davis
  • jeff_25
    jeff_25 Member Posts: 110


    a bare floor you can mist water on it when it warming up to find tubes evaporates faster at the tube
  • hr
    hr Member Posts: 6,106
    On a basic

    4" slab with the tubes mid depth, the wet method or heat gun will work fairly well. Start talking 6" or thicker commercial slabs and the tube location gets harded to pin point with these methods.

    John, it sounds like your method will show the tube regardless of the rebar or mesh? Makes sense as long as the aluminum is not touching the reinforcing somewhere.

    I believe the old Heatway Entran Trace had a hand held reciever to scan with. I don't see whay a wire installed with the tube couldn't be used the same way.

    As long as the two didn't part company :)

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • John Ruhnke1
    John Ruhnke1 Member Posts: 154
    How does that work...............

    John,

    Does the tracer send a electrical current through it? Do you need to connect a tracer to both ends and scan inbetween? Does the line finding equipment read just the traced line or will it pick up rebar and mesh too?

    JR

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Abostively!!

    Posilutely!

    Inducing current through alumipex. Just what I was gonna reccomend.

    However...If you believe that the tube is ANYWHERE near the top surface of the slab, where most light anchoring is done, then I have some land off the coast of Florida I'd like to talk to you about...

    The other alternative is infrared cameras. Quite accurate, and EXPENSIVE.

    ME