oil tank issues
todd_6
Member Posts: 13
I plan to place an outdoor tank near my shed. The distance is 100' from the boiler locaton which is in the basement say 10' below tank elevation.
PREVIOUS RESPONSE FROM THE WALL
If the tank is close to ten feet (or more) above the height of the burner you must use an OSV or PRV at the burner to protect the pump seals.
QUESTIONS
If you would not mind additional comment, would it be ok to place OSV at tank outside to provide better protection against line breakage? How does this device protect seals? Also you mention a PRV. Any specific model? Will just an OSV do the job? thanks, Todd
PREVIOUS RESPONSE FROM THE WALL
If the tank is close to ten feet (or more) above the height of the burner you must use an OSV or PRV at the burner to protect the pump seals.
QUESTIONS
If you would not mind additional comment, would it be ok to place OSV at tank outside to provide better protection against line breakage? How does this device protect seals? Also you mention a PRV. Any specific model? Will just an OSV do the job? thanks, Todd
0
Comments
-
outdoor tank
you are asking for trouble putting an outdoor tank that far from the burner an osv is a prv and must be protected from freezing so no it cant be outdoors where are you located
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
osv
so then, it would be best to put it inside the basement as the first device after the pipe passes thru the wall? Is another device a better choice than an OSV?0 -
oil tank
you still have not said where you are located and why the tank is so far away from the boiler plus what size oil line are you thinking of using
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
At what temperature does heating oil solidify?
Wouldn't you need to heat the oil line with tape or bury it to keep the oil from from gelling in really cold weather? I've heard this is a problem with diesel-fueled vehicles. A leak from a buried line could affect nearby well water and result in damages excluded by homeowner's insurance policies. Heating tape might not hold up very well outdoors.0 -
Not sure what the temp is..
But I used to live in a house in Michigan with oil heat and even up to -15F the fuel oil never jelled. Someone else probably has exact answer on this site - or maybe contact your fuel oil supplier.0 -
oil tank
the max run on a sunstrand pump is 100 ft with 0 ft of lift using 1/2 copper how do you propose getting to the burner i hope it will be thru conduit buried below the frost line in boston area thats 4 ft or so i hope you will burn kerosene rather than no2 fuel oil less chance of gelling
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
outside oil tank
I live in VA. I have burried copper 5/8 od 90' feet from house to shed area. Copper is type L sleved in black ABS coil stock. The idea was not to have an ugly oil tank next to my house. Our building code is CABO. I see that I need to read the code to see what safety devices are required by code here.
I want the ultimate in safety even if it exceeds CABO.
In this forum a year ago, it was suggested that an OSV was necessary to protect pump seals? maybe so, or not? The Beckett burner has a solinoid to shut the oil off already. That is why I was considering an OSV. Would you suggest other devices for safety in this install? I bought a LWCO already. Using burnham V8.0 -
outside tank
it would be easier to put tank near the house and build a shed to cover it according to the suntec manual 5/8 is good for up to 100 ft of run at 23 gph firing rate
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements