Hi guys,
are 007's normally OK for pumping (steam) boiler water? I've done it several times over the years, but now I have a job where the circ seized up a few weeks ago. I replaced the cartridge, no big deal. Boiler water was mucky ( new boiler, old system), so I did my best to drain out the muck and run some clean water though the boiler. I got another call over the weekend, I'll stop by there today. Same type of no heat complaint in the addition. Just looking for some input, if it's the same problem might I consider a 3 piece circ? All I'm doing is pumping into a flat plate hx, so there's just a couple feet of tubing on the boiler side. Thanks for the help.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=171&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
are 007's normally OK for pumping (steam) boiler water? I've done it several times over the years, but now I have a job where the circ seized up a few weeks ago. I replaced the cartridge, no big deal. Boiler water was mucky ( new boiler, old system), so I did my best to drain out the muck and run some clean water though the boiler. I got another call over the weekend, I'll stop by there today. Same type of no heat complaint in the addition. Just looking for some input, if it's the same problem might I consider a 3 piece circ? All I'm doing is pumping into a flat plate hx, so there's just a couple feet of tubing on the boiler side. Thanks for the help.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=171&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
try
a grundfos 15-42 pump, it has better starting torque but less max gpm which you dont need here, and if it's the right customer, you can show them how to remove the cap on the motor end, and unstick it with a screwdriver - a steam system is open to the air and is usually cruddy and the loop will always get gunked up, that's why they make boilers with built-in immersed heat ex's - if your boiler has one, use it - and if it's being used for domestic hot water - then feed it to the DMH AND to your heat-x with a priority zone valve controled by a waterflow switch - of course in this case, you will have to use a bronze pump, a backflow reventer, a mixing valve, and an expansion tank on the DMH side to protect the potable water supply
also if the house has a seperate hot water heater - it's usually cheaper to feed your basement heat-ex from it (again - with bronze pump, etc) - it's never easy, ..sorry0 -
The link below is to an article that B&G wrote several years ago about using the water from a steam boiler to run a hot water zone. We typically steer people away from a wet rotor circulator and towards a three-piece, oil lubricated circulator because of the problem that you're experiencing.
http://www.bellgossett.com/Press/waterzone.html
best regards,
Dan Schaffer
Bell & Gossett0 -
also
the B&G 3 piece out-starts them all and will seem live forever if you oil it correctly before every heating season,
30 years is not uncommon by me!!0 -
We always use the 3 piece pump
for pumping boiler water on steamers. However, we retrofit bronze impellers, when available. No plastics, or whatever the flavor of the month is.
The downside is the 1 AM "my boiler is blowing up" call when the coupler lets go. Why do they never break during the day?0 -
boiler water for hydronic loop
read dan's advice on a balancing leg between the supply and return to make sure that your loop is not running too hot...if it steams up the pump willfail quickly0 -
that is an awful noise
'bout a 7 on the sphincter scale.
Noel0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements