boiler size

rmn
Member Posts: 2
My heating for my house was converted to hydronic heatin/cooling. My HVAC man suggested for 4 zones with air handlers' tonnage at 12, the boiler size to be 294,158 btus. My plumber recently installed a new boiler with btus at 347,000. Is that too large? The boiler installed is Peerless with carlsin burner and storage tank at 60gal. thanks for your response.
0
Comments
-
The time
to do a heat loss is before an installation, the only way to determine proper sizing is to perform a heat loss calculation which will tell what you need. With relatively tight construction 350k BTU/Hr will heat an awesomely sized house,substantially bigger than your garden variety 5k sq/ft McMansion
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0