Check valve on inlet side of pump
Mr. Happy
Member Posts: 1
Is it okey to install a swing or flow check at the inlet side of a pump? Does it create enough turbulence to cause cavitation? Why do we prefer to install on the outlet side of the pump?
0
Comments
-
Placing a restriction on the inlet of a pump
is to be avoided.
Significant enough restriction at the inlet of a pump may cause the pump to cavitate - by dropping the available system pressure lower than the pump's required inlet pressure.
0 -
Be careful
with the piping and valves at pump inlets. Any devise that causes a drop in water pressure at the inlet may cause the pump to cavitate. This could include flow checks, throttling valves strainers, etc.
Of course the location of the expansion tank is also important for the same reason.
Low fill pressure and high operating temperatures are another thing to be careful of.
Always nice to have 6" or more of straight pipe before the pump, also.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements