This one got hot!
Rick Stevens
Member Posts: 1
Installed this boiler in 1997 (1,000,000 burnham) lack of maintenance caused low water cut off to fail in the "full" position. Boiler got cherry red and cracked end sections. Went with electronic LWC, wired in series with another LWC on the opposite side of the boiler. Lack of maintenance cost these guys $5,000. Just in time for Christmas!
Check out picutres of the completed job.
Check out picutres of the completed job.
0
Comments
-
HOT
Look at it this way ........ He saved at least 100 bucks on service!0 -
seems to me
I've seen those marks on that age of boiler before. Was that model known for roll out ?
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0