feeder valve for multiple boilers
Tom G
Member Posts: 5
I have three HW boilers heating three apartments. Can I feed them from a single feed valve? What if I install a one-way valve at each boiler, to isolate each of them?
Thanks
Thanks
0
Comments
-
common feeder
Unless the boilers are tied together in some way, you need a separate feeder for each boiler. A single feeder would add pressure to all the boilers if one lost pressure for any reason, and you would over-pressurize the others, blowing the safeties.
If the boilers are on a common header and are stage fired, one is enough.