Riello ???????? (SE)
Steve Ebels
Member Posts: 904
I have a Riello F-5 that has intermittent starting problems. When it fails to start, I can reset it and then briefly restrict the air to the burner by holding my hand over the intake. When I do this it will fire instantly. All parameters of a combustion test look good. Draft over fire is +.01", draft in the breech is -.04" (that's as low as I can get it) CO2 is 12.2%, O2 is 4.9%, CO is 3 ppm, 0 smoke. If I throttle the air back it will light off reliably every time but it also makes about a 2-3 spot on a smoke test.
What's going on with it? What am I missing?
What's going on with it? What am I missing?
0
Comments
-
What..........
boiler is it in? What type of nozzle? The Series 40 F5 seem to work best with Delavan "W" nozzles. Most of the ones I have use 60° spray patterns.
hb
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"There was an error rendering this rich post.
0 -
Make sure
your electrode gap is wide enough. Just a little bit wider than you normally think it should be.0 -
Check
Pump pressure and turbulator setting?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
What type of Unit?
with a draft loss of .05 thru the boiler? Is it clean?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Nozzle
Replace the nozzle....0 -
I
too have seen this when the burner cone is warp and
not perfectly round or in line with the blast tube.0 -
Riello
I had the exact symptoms on a Viessmann oil chassis burner a couple of years ago. Turned out to be a bad flare by the oil tank that would allow the oil to drain back into the tank and introduce a slug of air into the line. Do you have a Tigerloop on this?
Jeff0 -
Gap
check gap should be at 1/4".
had one 3 weeks ago, new install.. Having ignition problems called the local rep he told me to reset the gap from 4mm from thre factory to 1/4"...they changed the transformer..
0 -
It's on a Viessmann
Vitorond VR2-50. Gravity feed single pipe fuel line setup. Nozzle is a new(actually several) Delavan 1.10 60* A as per Viessmann spec. I have also tried Hago W series suggested by Viessmann. Pump pressure (175 psi) and all burner specs (turbulator @ 2.0, air gate @ 3.4) are nailed. I haven't tried the wide electrode gap. Where did that come from? Riello calls for them to be quite close. The boiler is spotless inside, it runs on low sulfer #2 oil at a steady 87%. There are also no problems with the burner head or cone.0 -
Set the electrodes with
the shaft of a standard #2 phillips screwdriver, works every time for me.0 -
You mean
Set 'em so the width of the shaft will slid between the electrodes? Roughly 1/4" gap?0 -
That's it. It's an old service trick
that I teach in my advanced Riello Seminar. So far, it hasn't failed me in 23 years.0 -
gap
use the magnet on that cute little screw driver Riello gives you. if it fits between the electrodes your gap is right.0 -
'nother ?
Does this electrode spacing apply to all F series burners or just 5's?0 -
F40-3 & 5 and M3,5,10,15,20
Steve, It is a fluke, not by design, but it is exactly the correct gap spacing. Also, just a thought, but 0 is NOT 0 on the turbulator disc setting bar. The first line is. So, a 2 setting is the third line. Probably you knew this, but just throwing it out there.
Jed0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements