pump head
Larry (from OSHA)
Member Posts: 745
I've got an indirect DHW with a high head HX. It is a Bradford White with 80' of .55" id tube inside the tank. The 3/4" copper to and from the unit is a total of 13' with 6 90* elbows and one Honeywell zone valve. BW wants to see about 3.5 to 4.5 gal. per min. thru it and a max of 5 gal. The system has one Taco 007 for everything. (4 zones including the tank). So is this in the ballpark or how do I calculate this out? Your help is as always greatly appreciated.
Wishing you all the best for a happy and healthy holiday season.
Larry
Larry
You've got to
get some more information from Bradford White. You need to know two things in order to choose a pump; flow rate in gpm
(which in your case is 5 gpm) and pressure drop in feet of head which is a function of the construction of the heat exchanger (HX).
Add up all the pressure drops (HX, piping, fittings, boiler, zone valve) and then go to your pump curves and choose a pump with a pump curve at or just above your point.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
- 125 Chimneys & Flues
- 120 Geothermal
