reverse return problems
ed wallace
Member Posts: 1,613
I recently repiped a burnham steam boiler that had a bad header set up i did a dropped header on it 1 rad was catching condensate in it even after it was pitched properly I installed a vapor stat now all is queit but takes for ever to heat up should i remove the dropped header or is there another solution ?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Vents
Have you checked the vents to see if operating properly or any missimg on the mains?0 -
Ed, where are the slow ones?
Near the boiler, or out at the end of the mains?
The dropped header won't be the cause, but the pressure might need a couple more ounces, or the boiler might need it's input checked against the load.
Noel0 -
reverse return problem
the only main vent is at the end of the run it has been changed out the pressurretrol is set for 16 ounces customer complaint is it takes 3 hrs to get rads hot but now the system is finally quiet
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Ed?
Is this thing oil, or gas? Could it be underfired? 3hrs?0 -
reverse return problem
the boiler is rated for 136,000 btus by clocking the meter its firing at 120,000 btus
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
What is the steam load?
0 -
Sounds like poor venting to me
as Noel said, the drop header ain't the problem. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements