Why Don't Some Pressuretrols Have A Pigtail?
Tom_22
Member Posts: 108
Why do some Pressuretrols sit on a straight pipe instead of a pig tail. Is either way OK? Is a Pigtail better? If so, why? For collecting sludge or dirt?
TomBk
TomBk
Pig tail
A pigtail will collect a puddle of water in it's lower loop which would and protect the control from steam damage. Why don't some have pigtail ? Have to ask the installer...0 -
$$$$$$$$$$$$$$$$$$$$$$$$$$$$$ a big fat dollar or two for a brass one Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
I'm going to change out the nipple to this pressuretrol tommorrow and put in a pig tail although it had a straight nipple and a T before, since it can't do any harm. (right?)
This is on a big old residential boiler that must be at least fifty years old. I think its an American something or United something, I forget. Can't hardly read the nameplate.
By the way, does anyone like to put a pressure gauge on the pressuretrol connections? How important do you consider that to check the actual performance of the pressuretrol settings?
TomBk0 -
Absolutely...try to get a gauge that reads in ounces too
protect them both with a pigtail. Mad Dog
My gauge is useless..
because it reads 0-30 psi. The needle never comes off of the pin. Never quite understood why such a useless gauge was installed.0 -
code
the gauge must read two times what the relief valve lets go at.
This is so that if the pressure rises above a faulty relief valve's setpoint, there is gauge enough left to indicate this condition.
Noel
So I see
said the blind man. Then I guess my plan to replace it with a useful gauge needs to be modified to leave the present gauge in place and install a useful gauge too! Thanks for the heads up!0 -
where to get gauges
You have a place where youm can get these gauges, because I need one for my mother's boiler, the people that installed the boiler gave my mother a busted gauge, I can't replace it because the boiler jacket has to come off and a whole bunch of other stuff.I have to install it on the pressutroll.Please post the make and the supplier of the gauge Thanks.0 -
Try here, all the gauges you'll ever need!
www.gaugestore.com0 -
Example of two gauges
See attached0 -
why two gauges
Why the two gauges? is the second one a backup ?0 -
thanks
thank you0 -
Is that new type
Is That a new type of pressuretroll above the two gauges.0 -
Sometimes
the boiler has a homemade pigtail . Take a look at Dan Foley's steam boiler under the post - Finished Steamer DF . I like to pipe the controls the same way when there is more than one , and also if there is a mercury controlled pressuretrol - theres no pontential of the pigtail moving when it heats up .0 -
Two gauges
One gauge is the stock WM 0-30 psi, code-required gauge. Since the blowoff is set at 15 psi steam, a 30 psi gauge is required. The second gauge is 0-5 ounces to help measure vapor pressure in the system. The control device is a Honeywell Vaporstat, which replaced the original Pressurestat.0 -
Vaporstat
Is the vaporstat the newest version of the pressuretro?0 -
Vaportstat
> pressuretro?
Vaporstat
No, I replaced the pressuretrol with the vaporstat myself when I added the ounce gauge. The pressuretrol was stock on my WM steam boiler. However, my system runs at such low pressure, approx 1 ounce, that the original pressuretrol probably would have been fine as a safety device. Due to the low operating pressure of my system, the vaporstat never cuts out, nor did the pressuretrol. The Vaporstat just provides me with a bit more insurance.
Because of the codes
You have a 30# gauge because the boiler and pressure vessel code requires it. Since you have a 15 pound relief valve the code requires that the center point ( most accurate portion) of the gauge read to the setpoint of the relief. It is NOT a good idea to remove that gauge it IS a good idea to install another gauge that reads for a 2 pound setting. Also in my building the system runs at 9 pounds for condensate lift. The boiler manufacturers aren't stupid so they install what's required.0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
