WGO-3 Circ Pump Piping

Rich Lee
Rich Lee Member Posts: 10
Weil Mclain Technical Service Bulletin SB0206, "Proper Location of the Circulating Pump", shows a diagram of a proper Pumping Away setup. My WGO-3 manual, page 15, shows a 1/2" "N" tapping for connecting the expansion tank, air vent, and fill valve. Should I plug this off and just use the 1 1/2" "C" (supply piping) tapping instead and "Pump Away"?
Thank you.

Rich Lee

Comments

  • John Abbott
    John Abbott Member Posts: 358
    The 1/2'' tapping..........

    may be used to vent the system by connecting an automatic "hyvent" vent to it or you may plug it off and use an air scoop or spirovent or its functional equivilant on the supply all will work despite what some overzealous wetheads might tell you.The Important thing is that you pump away from the expansion tank/boilerfeed connection.

  • John Abbott
    John Abbott Member Posts: 358
    The 1/2'' tapping..........

    may be used to vent the system by connecting an automatic "hyvent" vent to it or you may plug it off and use an air scoop or spirovent or its functional equivilant on the supply all will work despite what some overzealous people might tell you.The Important thing is that you pump away from the expansion tank/boilerfeed connection.

    John



  • David Sutton_3
    David Sutton_3 Member Posts: 160
    Hi Rich

    Rich, the way i found that works for me is..
    on the 1 1/2 put your circ and then up to your surply, on the 1/2 tapping go with a 1/2 x 3 nip then a 1/2 tee then a 1/2 x 1" nip then a 1/2 x 1/8 coupling then a air vent, off the tee go with a 1/2 x 5 nip then a tee then a 1/2 x 12" nip 1/2 90 the hang the extrol... off the tee build up your feeder then back flow the to your surplt from the cold water, hope you can follow this...David
  • George_11
    George_11 Member Posts: 11
    The tapping at the top of the boiler

    > Weil Mclain Technical Service Bulletin SB0206,

    > "Proper Location of the Circulating Pump", shows

    > a diagram of a proper Pumping Away setup. My

    > WGO-3 manual, page 15, shows a 1/2" "N" tapping

    > for connecting the expansion tank, air vent, and

    > fill valve. Should I plug this off and just use

    > the 1 1/2" "C" (supply piping) tapping instead

    > and "Pump Away"? Thank you.

    >

    > Rich Lee



  • George_11
    George_11 Member Posts: 11
    The tapping you are referring to is part of the feature of

    the boiler the directs trapped air at the top of the boiler to either an air vent--if you use a captive air tank, or if you use a steel tank to redirect air absorded into the water during an extended off-cycle back into the tank. Do not plug this fitting, as you will get an air pocket where one should not be. Do not install an automatic bleeder here if you use a steel tank.
    Mike