Just a question as far as header size goes. What if the manufacturer calls for a 3" header and you put in a 4" header. I would guess that a larger header is not bad. I am bidding a job that has an existing four inch header with 2 3" risers from an old boiler. I may be able to connect my 2 2" risers to this old header. Any comments would be appreciated.
Paul
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=280&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
Paul
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=280&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Your header size is going to depend on flow rate of total system 2" pipe with can pass 50 gpm which turns to be approx 500,000 btus at a 20 F temp drop
0 -
And if it's steam
no problem. Bigger is slower and better.
Noel0 -
Sorry
it is steam...thanks guys
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements