Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Hydro-Air in a Attic
Options
zibob
Member Posts: 8
We know they should not be up their to begin with, and yes it is almost scorched air, but a least it uses hot water, but we have a customer who has one, looking for solutions to blowing cool air from duct. It should be boxes in an insulated room and duct covered, but this may not be in the budget, has anyone tried fanhandler controls to run constant circulation? Any other ideas besides boxing and insulating ducts more?
0
Comments
-
hydro air
try adding a honeywell or white rogers strap on aquastat to keep the fan from running till hot water is running thru the coil if i hope there is anti freeze in the system
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
hydro air....
I put a strap on aquastat in the return line close to the coil that opens the zone valve and circulates hot water through the coil if the temp falls below 40*, I'd rather stay away from antifreeze0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements