Munchkin Problem??
Dave_13
Member Posts: 110
I have a friend who has a Munchkin 80M installed in his 2 year old home. Lately he has had problems with his "air proving switch" I would call it. It is locking out on this fault. It has been windy, so he tried to built a guard and shield it from the wind, but this hasn't seemed to help. Is this just a pressure switch that indicates that his combustion blower is running? Any ideas? Thanks
0
Comments
-
Hmmmm.
I thought someone would be on this quick!!!!0 -
Pressure switch
Quite a few of the Munchkins had pressure switches that were installed to the component board with screws that were too long; the screw pierced the housing and prevented proper operation. I had 4 of them.
Check with your supplier or the factory to find out if yours could be one of them. Have the purchase date and serial number handy.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
1 out of 6 are failing!!!!
I have had wholesalers tell me this. I talked to a contractor that has put in 40 of them and is having to many problems so he stop putting them in.
Ted0 -
Is it just the switch that has been the problem?? This one has a connector on the circuit board- there is no terminal strip that I see......0 -
The blower motor
goes out and switch and gas valve are the most common.
Ted0 -
shades of Voyager!!
Obviously the result of installer error!! Fool me once, shame on you; fool me twice, shame on me.
Bill0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements