Pump Location
Options
J Van Lund
Member Posts: 19
1) I have a small in-floor hydronic heating system (1500 sf) which has a Grundfos UP15-42SF circulator, which meets the system's circulating needs. We can mount it in a horizontal or vertical run of pipe. Will it perform better in the vertical run of pipe or the horizontal?
2) We read there should be a straight run of pipe equal to ten pipe diameters between the pump inlet and a 90 degree bend to avoid cavitation problems. So for a 3/4-inch diameter inlet pipe, there should be at least 8 inches of straight pipe before the 90 degree bend. Do you agree?
3) Should the same rule apply to the outlet side of the pump?
4) In a closed or dedicated system, does it matter if you pump toward the expansion tank or away from it? Everything we have read indicated that Rule #1 in hydronic heating is to always pump away from both the expansion tank and air separator. Do you concur?
Thanks for your help.
2) We read there should be a straight run of pipe equal to ten pipe diameters between the pump inlet and a 90 degree bend to avoid cavitation problems. So for a 3/4-inch diameter inlet pipe, there should be at least 8 inches of straight pipe before the 90 degree bend. Do you agree?
3) Should the same rule apply to the outlet side of the pump?
4) In a closed or dedicated system, does it matter if you pump toward the expansion tank or away from it? Everything we have read indicated that Rule #1 in hydronic heating is to always pump away from both the expansion tank and air separator. Do you concur?
Thanks for your help.
0
Comments
-
Some answers
1) Vertical or horizontal makes no difference, just make sure the shaft of the motor is horizontal.
2) Yes, I agree.
3) No; there aren't so many rules for the discharge side of the circulator.
4) Yes, pump away from the x-tank which is usually (but not always) attached to the air separator.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements