Pump Location

J Van Lund
J Van Lund Member Posts: 19
1) I have a small in-floor hydronic heating system (1500 sf) which has a Grundfos UP15-42SF circulator, which meets the system's circulating needs. We can mount it in a horizontal or vertical run of pipe. Will it perform better in the vertical run of pipe or the horizontal?

2) We read there should be a straight run of pipe equal to ten pipe diameters between the pump inlet and a 90 degree bend to avoid cavitation problems. So for a 3/4-inch diameter inlet pipe, there should be at least 8 inches of straight pipe before the 90 degree bend. Do you agree?

3) Should the same rule apply to the outlet side of the pump?

4) In a closed or dedicated system, does it matter if you pump toward the expansion tank or away from it? Everything we have read indicated that Rule #1 in hydronic heating is to always pump away from both the expansion tank and air separator. Do you concur?

Thanks for your help.