Pump Location
J Van Lund
Member Posts: 19
1) I have a small in-floor hydronic heating system (1500 sf) which has a Grundfos UP15-42SF circulator, which meets the system's circulating needs. We can mount it in a horizontal or vertical run of pipe. Will it perform better in the vertical run of pipe or the horizontal?
2) We read there should be a straight run of pipe equal to ten pipe diameters between the pump inlet and a 90 degree bend to avoid cavitation problems. So for a 3/4-inch diameter inlet pipe, there should be at least 8 inches of straight pipe before the 90 degree bend. Do you agree?
3) Should the same rule apply to the outlet side of the pump?
4) In a closed or dedicated system, does it matter if you pump toward the expansion tank or away from it? Everything we have read indicated that Rule #1 in hydronic heating is to always pump away from both the expansion tank and air separator. Do you concur?
Thanks for your help.
2) We read there should be a straight run of pipe equal to ten pipe diameters between the pump inlet and a 90 degree bend to avoid cavitation problems. So for a 3/4-inch diameter inlet pipe, there should be at least 8 inches of straight pipe before the 90 degree bend. Do you agree?
3) Should the same rule apply to the outlet side of the pump?
4) In a closed or dedicated system, does it matter if you pump toward the expansion tank or away from it? Everything we have read indicated that Rule #1 in hydronic heating is to always pump away from both the expansion tank and air separator. Do you concur?
Thanks for your help.
0
Comments
-
Some answers
1) Vertical or horizontal makes no difference, just make sure the shaft of the motor is horizontal.
2) Yes, I agree.
3) No; there aren't so many rules for the discharge side of the circulator.
4) Yes, pump away from the x-tank which is usually (but not always) attached to the air separator.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements