3/4\" trinity
mark_20
Member Posts: 9
I was looking at installing a Munchkin 199 for a radiant heat project (4500 sq ft home). My supplier told me it is on backorder for two months and suggested a Trinity 200. I have a concern about the 3/4" supply and return and how it will effect the system. Any thoughts?
0
Comments
-
I just...
...installed my first Trinity last week. I, too, was a bit surprised by the 3/4" connections on first glance, but upon thoroghly analyzing the makeup of this boiler, decided I was comfortable with it.
The biggest thing you need to do is to make sure you have proper flow through the boiler. The installation manual specifies the head loss of the boiler itself, along with the required flow rate. Just add your piping losses to that, and make sure you properly size the circulator. IMHO, primary-secondary is the way to go, with the boiler in series with the primary loop.
Overall, I was very impressed with the Trinity - see my post below. Good luck,
Starch0 -
Trinity flow
Use Primary-Secondary with a 0011 or 26-99 and you'll get the flow. Piping will make or break your job. Enjoy...Dan
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Here's a pic...
...of my shop boiler.
Starch0 -
Hi Mark
What I do is increase piping to 1" right away going into the primary loop.It just seems easier to work with.
Good Luck
Brian0 -
Thanks for the info and especially the pictures they really help. Since i have not yet heard any negative response I think the trinity may be the way i go.
Thanks again
Mark0 -
199 munchy
Contact Marc at Radiant Heat Supply 610 466 7875. I believe that he has them in stock.0 -
199 Munchkin
Mark:
I have 199 Munchkins in stock.
Marc Sherby
Radiant Heat Supply
610-466-0500
610-466-7875 FAX0 -
I use lots of Trinty's. Very little problems. It really is a copy of a chipmunk, same heat exchanger, although HTP will tell you that Trinty uses a smaller exchanger that the Munchkins do. Primary/secondary is a must, and I use flow switch on every one. At our elevation (5280 ft) a combustion analyzer was needed to get it to burn right. These boilers come with built in outdoor reset and DHW priority. My local supplier can not keep them in stock they sell so many of them.
Dave Stroman,
Stroman Plumbing and Heating,
DenverThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements