New Burnham Steamer on Ideal Vapor System

steve_6
steve_6 Member Posts: 243
this system has adjustable seats in its radiator traps. Does anyone know how they should be adjusted???? I posted some pictures of the traps also!!

Comments

  • Steamhead
    Steamhead Member Posts: 17,507
    Looks like they just screw in

    but if the threads go all the way thru the trap bodies, try setting them so there is about 1/16" between the element and the seat when the trap is cold.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • steve_6
    steve_6 Member Posts: 243


    yes the threads do go all the way through the trap. I'll try that adjustment. thanks