New Burnham Steamer on Ideal Vapor System
steve_6
Member Posts: 243
this system has adjustable seats in its radiator traps. Does anyone know how they should be adjusted???? I posted some pictures of the traps also!!
0
Comments
-
Looks like they just screw in
but if the threads go all the way thru the trap bodies, try setting them so there is about 1/16" between the element and the seat when the trap is cold.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
yes the threads do go all the way through the trap. I'll try that adjustment. thanks0 -
nice piping work steve..
as usual...sorry i missed out on that job..you can turn those pictures 90 degrees using microsoft paint which may be on your computer already..oh, i snagged you an old mouat thermostatic trap to compare with those ideal traps today..i'll give it to you next time we cross paths..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Ray Make it look like this
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements