Cast Iron Radiator Conservancy

Dan, (or anyone else) is there anyway I can use your EDR book to look up the btus of a given C.I. Rad and give it an equivalent baseboard fin tube value, eg I was trying to explain to someone that removing the freestanding rads is not an energy conserving move. Is there a formula I can use on the job to say to a customer...yeah if you remove this X-size radiator youll need xyz feet of fin tube to replace it. I dont think I should have to do a heat loss to figure that general equiv. Any Ideas?

Thanks,

Rich

Comments

  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Sure ,from my rad pad

    170 degree water going into rad = 150 btu per sq ft edr

    180 " " " " = 170 " " " "

    190 " ' " ' = 190 " " " "


    You can calculate from there.

    If you had a radiator with 5sq ft @ 180 degree water you would have 800 btu's dived by 580 btu's per ft for (average) baseboard to give your equivalent baseboard length.