NON-FERROUS COMPONENTS
DaveGateway
Member Posts: 568
I'm trying to design a totally non-ferrous hydronic system.
I'm having trouble finding an expansion tank that doesn't have steel in contact the hydronic water!
Even the double diaphram Amtrol doesn't prevent this!
Also boilers?
The MZ boilers do have steel in contact with the water!
Does the Munchkin? Any other condensing choices?
Thanks for any help
I'm having trouble finding an expansion tank that doesn't have steel in contact the hydronic water!
Even the double diaphram Amtrol doesn't prevent this!
Also boilers?
The MZ boilers do have steel in contact with the water!
Does the Munchkin? Any other condensing choices?
Thanks for any help
0
Comments
-
potable water x-tank
won't do the job? Just let the pressure down to 12psi or as req'd.0 -
boiler options
Munchkin, Trinity, Vitodens, Baxi, Takagi, Rinnai ...... you have many choices. Why non-ferrous? Enjoy.......Dan
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
NON-FERROUS COMPONENTS?
Scrook,
Would a potable water x-tank meet code?
Thanks0 -
NON-FERROUS COMPONENTS?
Dan, thanks for the input.
NO steel internal components, that contact the water, in all those boilers that you listed?
My reason for non-ferrous is cost!
Both the Wirsbo & Kitek manuals state the their non-O2 barrier PEX will work just fine IF all components are non-ferrous.
The savings on the cost of the PEX will pay for the bronze pumps.
Thanks0 -
Another answer
would be treat the system with Rhomar 922 which has an o2 scavenger in it as well as multiple metal corrosion inhibitors. As long is the level of treatment is kept up
(a yearly ck up) this would allow you to use the boiler of your choice. On the other hand saving on the pex tubing may not allow you all the choices that are available.
0 -
Non-Ferrous
The Munchkin has a 100% stainless steel heat exchanger. The only other material involved on the water side is the brass on the sensors and the brass supply and return nipples.
Hope that this helps.0 -
I have used
potable water expansion tanks, also. Check the temperature rating, mine have all been low temperature radiant, which run cooler than most DHW.
Reduce the pressure, and get a 3/4 X 1/2" brass reducing coupling to connect them.
You might get the manufactures spec sheet and blessing if code compliance is an issue.
Plenty of non ferous heat sources. I see Lochinvar now glass lines the cast iron headers on their hydronic boilers, making them non ferrous, kind of.
hot rod
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Stay conscious..
Be sure that the tubing you purchase is cross linked. Many of the COLD water tubing is a straight PE pipe and not rated for heating temps. I'd spend on tubing and do it right the first time - it's permanent! If you want to shave pennys you can reduce the # of zones or consolidate controls. Enjoy....Dan
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
NON-FERROUS COMPONENTS?
Dan,
Both the Wirsbo & Kitek manuals state that their non-O2 barrier PEX will work just fine IF all components are non-ferrous! PEX = cross-linked polyethylene! Its not pennies, its about $150.00 - $250.00 / 1000' of 1/2"
Thanks0 -
NON-FERROUS COMPONENTS?
Hot Rod,
thanks for the input. I was unable to extract the upper temp. limit for a DHW X-tank from Amtrol's clunky web site! I could hang a 50' loop of leftover PEX up by the TJIs to cool the water before it enters X-tank?0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements