Vaporstat model
btc
Member Posts: 43
Im convinced. Want to put vaporstat on my single pipe steam, 135,000BTU gas fired boiler. Currently using old PA404A.
Any recommendations on the specific vaporstat make/model number to consider--there seem to be numerous choices--many of which seem to only have subtle (but meaningful?!)differences.
Thanks.
Thanks.
How well vented is your system?
If it is average, I'd opt for the Honeywell vaporstat that has a range up to 4 psi. If you can , though vemt with Gorton #2s and go for the Honeywell Vaporstat that goes up to only 16 ounces (L408A). Mad Dog
Thanks for the response. I have Gorton #1's at the end of each main (20 ft each way with 2" mains). Have been considering Gorton #2's. Is there any problem increasing the venting rate--is there such a thing as too much venting at mains?
Thanks. Brian0 -
never to much venting,,
mad dog has a rack of gorton 2's on his..you can see it at hvactv..really sweet0 -
no, you can not vent too much
sometimes radiators venting rate needs to be slowed down, but the mains.....let 'er rip. I might add more too , Gerry! Mad Dog
L408A Vaporstat
is available as 0-16 oz./sq. in. w/ 2-16 oz./sq. in. subtractive differential and as 0-4 lb./sq. in. w/ 4-16 oz./sq. in. subtractive differential, SPST Break on pressure rise. The 0-4 psi unit would let you go to 1.25 or even 1.5 psi cutout w/ a 1 psi differential, which might be handy if your main vents are small, but the 0-1 psi (0-16 oz) unit would prevent setting the pressure too high. Either should be much easier to set than a PA404A at low pressures. You could keep the PA404A, put it on a seperate pigtail and set it to ~3 psi cutout as a safety limit should the vaporstat fail closed.0
- 129 Chimneys & Flues
- 122 Geothermal