I am trying to decide if my system would benefit from the installation of a buffer tank to improve the overall efficiency and I am looking for input from The Wall experts.
My Buderus 124X gas fired boiler (108K BTU o/p) is piped primary/secondary and serves an indirect DHW, high temp baseboard and panel radiators as well as 3 radiant zones (injection mixing). A Tekmar 371 paired with a 369 controls everything and the high temp zones are set back during the day and overnight so a good part of the time the radiant is the only demand. During these times the boiler short cycles (1-3 minute runs) and I figure this can't be good long term.
Would my system benefit from a buffer tank? If so, how would I pipe it, how big should it be and how do the temps in this tank get controlled?
Thanks guys!
Thanks guys!
What is the heat load
was a heat loss calc done?
This would tell you how closely the boiler output is matched to the load of the building. Generally oversized boilers are the main reason for short cycles, if all the current controls and thermostats are set correctly.
The smaller the load the more the boiler will cycle, unless it modulates or has a high water volume. Or a buffer tank
The boiler may have been up sized to provide plenty of horsepower for the indirect.
All the answers are in the numbers, what are they?
hot rod
Total heat load was approx 137K at a design temp of 80* (high, I know) when whole house was cut over to hydronic. Most of house now is hydronic although FHA still heats part. Radiant zones are small bath (2K), sunporch (22K) and family room (18K). Does this help?0 -
More questions
How are you controlling the FA and radiant zones? Does the FA also heat into the radiant zones? Or are they seperate rooms closed by doors? Or 2 stage t-stats.
Here is some buffer calc First let's call your load 42K with all zones running. Assume a current 5 gallon buffer, considering piping, etc.
With a boiler at 180-140° setting, the boiler in a 65°room, water as the fluid The computer suggest a run time of 1.5 minutes on and 2.3 minutes off.
Now add a 50 gallon buffer tank (18" in diameter)with R-8 insulation around the tank. Again 65° boiler room temperature. Same 42K load
The program now shows a 14.8 burner on cycle and a 23.3 minute burner off cycle.
Try some other tank and load inputs at www.hydronicpros.com An excellent software program to own can be demoed and purchased there. Excellent for design before starting a project, also an excellent troubleshooting tool to show, in living color, what exactly is going on with a system, and how it can be effected
hot rod
Answers to more questions
Yes. The FHA does suppply some heat to 2 of the 3 radiant zones. They are not seperated by doors. The FHA runs on its own Tstat. The radiant zones are each controlled by RTUs connected to the Tekmar.
Thanks for the suggestion on the software. I see that the total run time in the 5 and 42 gallon is approx the same but it gets there by "short cycling" in the case of the smaller tank. Although example was with a high/ow setting on the tank of 180*/140*, I would assume outdoor reset would work the same because the target temp for the boiler set by the Tekmar would be what the boiler heats the water in the tank to? How important is the wide (in this example 40*) differental of the tank setting? Typically the Tekmar outdoor reset tries to control the boiler temp within a tighter range.
Now a question of how to pipe a tank. Does the boiler heat the water in this tank and then the tank supplies all the water to all the heating zones, high and low (radiant)? Kind of just like an indirect on DHW? And like an indirect DHW tank, does the boiler water circulate through a coil inside a buffer tank or does the water all just mix in the tank? And I would assume that the DHW load supplied by the boiler has nothing to do with this tank so that off season you are not heating the buffer tank to heat the DHW tank.
Sorry for all the questions. Just trying to understand all of the issues involved. Thanks.
I am still
trying to figure how the FA and radiant get along. Is the FA thermostat in the same room with the RTU's. doesn't the FA over run the radiant, as it responds quicker?
Anyway, there are a number of ways to pipe a buffer. Series is a very simple way, better suited for condensing equipment. I've done some parallel, (Neanderthal drawing #1, below) keep the tank fairly small as the cold tank will lengthen start up time from a cold start. I have done this arrangement with the 20 gallon HTP buffer tank. On low temperature distribution run a wide delta T maybe 140-180 in the tank for long cycles and small piping, and injection mix, or whatever off the buffer. Again, protect the boiler return.
A couple P/S arrangments. This allows the most flexability, could fire the indirect without using the P/S loop in summer modes, and could supply various secondary temperatures.
The bottom drawing shows a variable speed pump injecting into the primary loop. Maybe your current tekmar could drive this method? Controlling the whole "ball o wax" takes some thought and pen to paper time!
hot rod
Say HR, I'm looking at buffering my QL
When you say in series, would that mean pipe the boiler output into the bottom of the tank and then the top of the tank out to the system (piped P/s). I imagine you want to keep the indirect piped directly to the boiler for quick response. I plan on using a Triangle tube Smart 60 with 24 feet of heat transfer area).
BP0 -
I agree BP
The MZ in my shop/ office is piped like this. It has the intergral HW maker, however. It does have a longer start up, but I only need 98° temperature. It is a small buffer 36 gallon, I believe.
Also water gets circulated through an unfired boiler, but the HX is very small capacity and the stack loss must be small on a vent inducer appliance.
hot rod
Trying something similar
I have a roughly 45 KBTU heat load but a fairly mild climate (costal Pacific NW). I could have the same sort of loads of just a few KBTU with the same short cycle problems. I want to combine the buffer function with the indirect DHW (e.g., single tank). I will probably be using a Munchkin 85. I was thinking 45-100 gal indirect tank.
My intent is to circulate only boiler water in the tank but that is not an absolute requirement.
Does a combined function tank make sense? Can you sugest sizing?
What might work better
Is putting the buffer on the return from the space heating zones. I have a Tekmar 371, so I would want to install the sensor on the supply so it could read both the supply to the system and to the DHW unit. I've got my boiler pipe P/S to the zones, so it will only circulate when their is a call for more heat in the system. Oh course then it wont see the system temp for reset..... HMMM. Just starting to think about this one.
Buffer tank on the return would alos mean lower standby losses due to cooler tank, methinks.
How do you like the MZ? I am planning on taking on some condensing equipment now that gas prices in Northern IL are closer to the rest of the country (gas peaked at 33 cents mid winter from 79 to 98... 0% inflation, so efficiency wasn't an isssue until recently)
BP0 -
I think
for storing BTU's I prefer hot water
Your idea would help the run cycle length, if controlled properly, but it wouldn't store much heat at return temperatures, if I follow your thoughts.
hot rod
Yes
I think you have a concept that works, in mind. See if you can get a copy this John Siegenthalers ISH presentation. I think the system you are dreaming is in this 20 page handout.
Siggy is very generous with his materials
With his permission I could fax a copy of this copyrighted material.
hot rod
Yes, all I am looking is for cycle length
since I don't need to "buffer" a high temp boiler from low temps. Since the delta tee in the tank would be the same whether supply or return, it doesn't make a difference how hot the water is. Water stores the same amount of heat going from 70 to 90 as it does going from 140 to 160, more of less.
BP
BP
yes it is true the same amount will be stored at the lower temperatures, it's in the delta T, even with chilled water.
My point about the warmer temperatures is the widddder delta T. If your emmiters can operate at those low temperatures, running say 140-150 in the buffer then pulling it down to that 70 or 90 would spread the delta T and help with the cycle length even more. If the cycle lengthn is more important than the stand by loss for the tank temperature?
A well insulated tank with 2" of foam in a heated space would still offer some good BTU storage at 140.
It is fun playing with the various options.
DVW had a plan to run a buffer up to 180, and pull it down to 80 for a 100 degree delta t on a radiant slab application! Be interesting to run some pipe sizing and buffer time cycles on a system like that.
hot rod
Is there a downloadable version of the presentation available anywhere. I tried searching but could only find references to the fact he was giving the presentation.
In an unrelated note - is there anyway to see the whole forum contents. All I get is the last three days and I have not been able to find any way around that. I am also having trouble getting to the forum. I keep getting file not found messages. And there is no contact information for the webmaster. If some of you regulars could provide some insight into this it would be appreciated.0 -
Look for Siegenthaler's articles
archived under P&W mag's website:
www.pmmag.com
He also has an excellent article and software on his website
www. hydronicpros.com
There's a number of reverse indirect makers that would give you both DHW and buffering:
www.ErgoMax.com
www.dunkirk.com (Artesian)
www.thermo2000.com (TurboMax)
www.laars.com (DuraFlow)
www.tfi-everhot.com (EA series)0