melt down

lchmb
lchmb Member Posts: 2,997
Had a call the other day where the customer complained of a smell from the boiler. Upon arrival the h/o indicated that the boiler had been making hissing sound's and banging for a week or two...He also stated that he could hear a waterfall sound every now and then..Upon inspection of the boiler we found that the casing had actually melted and that the boiler was dry..It had split the casting in a number of location's. It was a Weil Mclain with a triple aquastat..Guess they can run without water for awhile..In the two week's it had run the temp was down in the teen's..
Stay warm
BTW..the new boiler now has a low water cut off...maybe they should become standard with new boiler's...worst part was this boiler was only a year old...pile of scrap metal now....

Comments

  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Got pictures???

    ME
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Poor little JV


    Saw one like that a few years back.

    Boiler was installed in a pool room closet and was used to heat the pool.

    May it rest in peace.

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • clammy
    clammy Member Posts: 3,181
    Hey Mr.Earthton

    Hey mark are those pictures of a teledyne lars mini therm? just wondering?

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Yes, T/L MiniTherm...

    There was a leak in the heating system. The "competition" that intsalled the boiler in the first place replaced it three times in 4 years, not under warranty. Not one of them mention to him that they thought there might be a leak in his heating system....

    When he called me on the phone to ask my opinion, I listened to his tale of woe, asked a few questions and told him there was a leak in his system. He was on well water, HARD well water.

    I replaced the boiler with a cast iron boiler that could be fired without circulation, kept it hot and pressurized and he found and repaired his leak. System now has a low water fuel cut off device, a low pressure cut off device, and no solid connection to the make up system.

    Some peoples kids...

    ME
  • lchmb
    lchmb Member Posts: 2,997


    only have a pic of the triadicator...pretty much say's it all
  • jim sokolovic
    jim sokolovic Member Posts: 439
    Is that...

    one of Salvidor Dali's works?
  • Billy_3
    Billy_3 Member Posts: 42
    Mark

    Did that boiler have a flow swith on it?
  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    NO flow switch... (NM)