PAINT SPRAY BOOTHS MAKE UP HEAT

I NEED TO KNOW IF ANYONE HAS ANY KNOWLEDGE PERTAINING TO MAKE UP HEAT IN SPRAY BOOTHS. WORKING ON JBI INDUSTRIAL AIR SYSTEMS WITH POWERFLAME C3 BURNER. HAVING SOME PROBLEMS WITH UNIT WANT TO KNOW IF ANYONE OUT THERE HAS HAD ANY WITH THESE PARTICULAR UNITS. THANK YOU

Comments

  • DaveGateway
    DaveGateway Member Posts: 568


    Have you tried powerflame.com? where are you located?
  • sinkdoc 4338
    sinkdoc 4338 Member Posts: 11
    PAINT BOOTH MAKE UP HEAT

    I AM IN THE PHILADELPHIA AREA. CONTACTED POWERFLAME WITH NO LUCK.
  • Don Walsh
    Don Walsh Member Posts: 131


    What particular problem are you having? It is critical that your gas supply pressure be exact, the units we have serviced needed a constant 11" pressure while firing.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Kevinj
    Kevinj Member Posts: 67
    JBI

    Have you contacted JBI for help ???
  • Jeff Krawic
    Jeff Krawic Member Posts: 58
    PowerFlame make-up air

    Yup worked on a few. Let us know what the particular problems are on this one. Maybe we can be of some help. Also you may want to contact Bradley Sciocchetti Inc in Merchantville, NJ These folks are the PowerFlame rep. in your area if I am right. John Rex is a tech there and he is pretty good. Phone number for Pa 610/523/5373
  • sinkdoc 4338
    sinkdoc 4338 Member Posts: 11
    paint spray booth make up heat

    JBI IS NO LONGER IN BUSINESS, UNIT IS OIL FIRED WITH SPARK IGNITION. UNIT LOCKS OUT ON FLAME FAILURE MORE THAN IT SHOULD,IT IS UP ON THE ROOF OF THE BODY SHOP. THE FLAME GOES OUT DURING OPERATION FOR NO APPARENT REASON, IT IS FITTED WITH A INDUCED DRAFT FAN.
  • Kevinj
    Kevinj Member Posts: 67
    Look here

    FIRST, TURN OFF YOUR CAPS LOCK. Then see where JBI went....

    http://globalfinishing.com/

    Now if the oil burner goes out during operation and not on ignition you have very few things to check. Oil supply comes to mind first and the maybe controls or wiring.