taco or honeywell zone valves
Big Ed
Member Posts: 1,117
Less known problems with Honeywell.
0
Comments
-
should I use Taco or Honeywell zone valves for a residential job with six zones and two pumps with cast iron baseboard hot water heat. The price seems to be about the same.
0 -
I too prefer the honeywell
zone valves. I have had newmerous problems w/ taco 271 right out of the box...I also don't like the slow open/close either...However the taco zone valve controls zvc series are tops in my book..would be great w/ a sr502 relay...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
We .......
have installed taco 570 series zone valves for 25 years with very few problems.The design is a marvel of simplicity and function.I have tried other brands and models but have gone back to the 570 series even on high end radiant systems.They are reliable available and they work.I had in the PAST serious problems with Honeywell zone valves caused by their design but that may not be at all relevent today.
John0 -
Taco Zonevalves
Taco, zonevalve bodies are warranteed for 5 years, and the actuator three years. They have beem proven to reliable over the approx. 40 years in the field. Additionally, taco offers technical support for 570 series zonevalves, and all other products. Please advise, if you have any specific questions or concers regarding Taco, products.
Joe Mattiello
Technical support Technician
401-942-8000 X 484Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
zone valves
i to prefer taco zone valves. i have had very good luck with them. if you are pumping away with your piping i would put the zone valves on the return this will eliminate any possible valve lifting due to the power of the pump
good luck joeg.0 -
The spring...
on the taco 570's is strong enough to resist lifting from even high head pumps we always pump away.Even on commercial jobs with 0011 pumps we have never had one lift. Your concern is legitimate Joe but it is safe to put them on the supply.
John0 -
Waatch your wiring
I recently installed taco 3 wires, wired by electrician,, the homewoner updated the thermostats to new honeywell t87 digital,, - these have a resistor in thepackage ( box from supply house) to install on 1 & 2- if the wires are backwards- the display will go blank.... Also these same t stats from big orange store w/ sub base don't come or mention the resistor, identical, but the back of the package says for two wire only.0 -
john
thanks john for the info. i havent had this problem yet , but i havent used a high head pump.
thanks again joeg.0 -
the biggest reason to put the ZV on the return.....
(when pumping away)is to reduce /eliminate the zone valve pressure jump bang. Yes Honeywells are more suceptible to this but it can happen w/ any zone valve in a multilpe call situation, etc, etc..... I usually prefer circs especially now that they have IFC's out... kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I have many of each..........
installed over the years and both brands are relatively trouble free. They are very different in how they work and how they are wired. I wish I could type as well as others here do. It just takes way to long when you are a hunt and peck typist and have a lot to say ;-)
hb
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
it is because of the .....
wiring, that can get tricky, is the reason I use the Zone valve controls....plug and play! very clean, lets you prioritize and the lights are very cool as well as letting you know what on at a glance... kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
wiring
yes the taco controls make wiring a snap but every tech should learn and understand how they are wired. this will make us better troulbe shooters.its like having a calcultor and someone shows you how to make it add,subtract,multiply and divide but take the calculator away and we are lost. iam not trying to be a smart **** just making a point.
joeg.0 -
The ....
taco 570's close VERY slowly and I have never experienced any banging or pressure jump under any circumstances.The Honeywells on the other hand are a different story even if the flow is in the right direction.
John0 -
You........
make an excellent point Joe. We should all try to understand function, wiring, and trouble shooting of simple electrical devices without the benefit or need of a control with leds they are not always available on a no heat call.
John0 -
Birds Nest
I will look into the plug & play set up . I dislike the wiring on a group of zonevalves . "Birds nest" , Trying to clean up the mess without spending a lot of time is troublesome . I also like to add little lights to the job .
Sounds like alot of fellow Wallies are happy with Taco. I will give them a try when I have the chance......0 -
The thing to remember............
about Taco 571 zone valves is their amp draw. The specs say .9 amps, but most I have measured will pull over an amp on start. Also, consider using a 50 VA instead of the 40 VA Transformer per three 571s. When three valves are opening simultaneously, they use in excess of 60 VA temporarily.
hb
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
You are........
100% correct heatboy. They draw 1.1 to 1.2 on my meter and you must set heat anticipators accordingly or you will get short cycling and undershooting of thermostat settings.I feel really stupid for not mentioning that.I like the idea of the 50 VA transformer.
John0 -
Amp Draw
What is Taco's amp draw reading on "fully open"??0 -
I thought we were....
talking installation, done once and done right? kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
+
> talking installation, done once and done right?
> kpc
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 323&Step=30"_To Learn More About This
> Professional, Click Here to Visit Their Ad in
> "Find A Professional"_/A_
0 -
We.....
are exchanging information and opinions Kevin .I thought that the wall was the proper forum for that. If I am wrong please correct me.
John0 -
The amp.........
> What is Taco's amp draw reading on "fully
> open"??
0 -
The........
zone valve full amp draw cycles on and off when fully open as the heat motor cools the switch makes momentarily and then breaks when fully open.This cycle continues until the the thermostat is satisfied.The heat motor is a beeswax filled cylinder heated by a resistence heating element around it.When fully open it makes an end switch to start the circ/burner and breaks a switch to the heating element which makes and breaks to keep the valve open during the call for heat.So one minute there will be no current then for a few seconds you will draw full amperage. This is why some power robbing thermostats require a resistor with the 570.
John-1 -
no correction needed...nm
have a great day John!...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
no correction needed..
have a great day John!...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements