Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
rewire 8184M control
Doug@ASI
Member Posts: 1
Just wondering if anyone out there knows how to replace a 8184M with a 8184G and seperate transformer. Just need low voltage wiring help,thanks.
0
Comments
-
try to explain
a couple ways. Install fan center. R from center to T-stat. W from t-stat to one side of general purpose relay coil. other side of coil to common on fan center trans. From TT on 8184g to normally open side of general purpose. G Y go where they go. Easier to carry an m but this will work.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
An easier way maybe?
Carlin has a "kool kit" so you can replace a "m" with one of their controls. The kit comes with a board that goes under cad cell, this way you have somewhere to connect the wires to w/screws vs wirenuts.It comes with a transformer. Nice set-up and if cad ever needs replacing it will be quick. John@Reliable0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements