rewire 8184M control
Doug@ASI
Member Posts: 1
Just wondering if anyone out there knows how to replace a 8184M with a 8184G and seperate transformer. Just need low voltage wiring help,thanks.
0
Comments
-
try to explain
a couple ways. Install fan center. R from center to T-stat. W from t-stat to one side of general purpose relay coil. other side of coil to common on fan center trans. From TT on 8184g to normally open side of general purpose. G Y go where they go. Easier to carry an m but this will work.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
An easier way maybe?
Carlin has a "kool kit" so you can replace a "m" with one of their controls. The kit comes with a board that goes under cad cell, this way you have somewhere to connect the wires to w/screws vs wirenuts.It comes with a transformer. Nice set-up and if cad ever needs replacing it will be quick. John@Reliable0