one pipe venting
Options
ray mroczenski
Member Posts: 3
I'm thinking of replacing the radiator vents on a one pipe steam system in a 3 flat. I want to install Danfoss Trv's instead. I know not to put one in the room with the stat. My question is: Do I need to be concerned with the size vent to maintain adequate steam to all the radiators? Do I install different sizes vents on different floors? I've already installed these in the 2nd floor apartment with great success, and only used Dole 1933 straight/non adjustable vents. Will this retrofit work throughout the building? Thanks for your help.
0
Comments
-
That should work well
and if any radiators prove to be slow to heat, try a Hoffman #41 vent.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements