Can anyone tell me how to figure the GPM's thru a 3/8 copper tube at 100psi.
0
Comments
-
100psi drop...
or max acceptable flow through a 3/8" tube (at 100psi or other)? A 3/8" O.D. should tolerate about 1.5 GPM max long term, maybe a little more intermittantly. Pressure won't effect the max acceptable flowrate for liquids, though the resulting pressure drop may be excessive, depending on tube size, length, inlet pressure, and required outlet pressure.0 -
Water?
at 70°F flowing at max acceptable velocity of 4fps (CDA) would flow 2 gpm. Fine for continous use. You could push 2.5 or 3 gpm intermitantly with velocity of 6fps.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
those are good numbers as listed, they are taking into account noise from the water velocity. you could push a little more through there, but it will be noisy.0