Hydronic loop from steam boiler...JohnNY
JohnNY
Member Posts: 3,293
How many of you use bronze body pumps on your steam boiler hydronic takeoffs? B&G recommends it in a big way. Is this just a way to sell up? They also only recommend using the 100 series bronze body.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=290&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=290&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
0
Comments
-
I don't
what about all the steel and cast iron the condensate contacts passing thru the boiler? Its crap, John...looking foward to seeing you at the CO class. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Hi John
My experience with this is that the Series 100 B&G or 110 Taco bronze pumps perform better and last much longer than the wet rotor pumps in steam applications. As far as I know, the passages are a bit more forgiving with the sediment that is usually present in steam systems as well as the pump impeller and housing holding up better to the high temperatures. I've been on countless jobs where wet rotor pumps have failed after a year or so and the bronze Series 100 or 110 cured it every time. Just my thoughts.
Glenn0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements