Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Two-Story Riser on One-Pipe Steam System
Steamhead
Member Posts: 17,504
1. The riser is undersized for the amount of radiation on it.
or
2. One of the runouts from the riser to a radiator is off-pitch, trapping water.
or
3. The air vents on the radiators are too big and condensate can't drain back against the rushing steam. This condition can also be caused by a missing or too-small vent on the steam main.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
or
2. One of the runouts from the riser to a radiator is off-pitch, trapping water.
or
3. The air vents on the radiators are too big and condensate can't drain back against the rushing steam. This condition can also be caused by a missing or too-small vent on the steam main.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
Two-Story Riser on One-Pipe Steam System
HELP!
I have a steam riser running from the basement boiler to the finished attic in my two-family house. It is the only pipe with water hammer, the water hammer is during start-up mostly. The pressuretrol is set to about 1.5 psig. The other risers (though only going to the second floor) have no water hammer. There are two radiators on this riser. I cannot see the piping completely, but it is probably a tee at the top of the riser in the attic floor with branches to the radiators. The radiator air vents are venting OK, no steam spitting out. This riser is the closest to the boiler. The boiler was replaced before I bought the house, looks about 10-15 years old.
Any suggestions on what to check or adjust?
My first floor tenant is going bonkers!!!
THANKS!
0 -
Water Puddle
Try raising both of the radiators and make sure radiators are pitched to the supply pipe.. Water is laying some where.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements