weil mclain lwc
MIKE6
Member Posts: 102
Utica 112,500 gas spark ignition with an electronic low water cut off.This unit is 1 month old,cust finds a no heat condition,unit shows red light low water condition BUT unit 's gauge glass shows water at half way level. Unit doesn't surge.Installer came twice and cleaned boiler water and pulled lwc probe and cleaned.Unit fires after resetting service switch.any ideas
0
Comments
-
Probe
Make sure 1st 2 threads on probe do not have dope or teflon tape on them.Might be a bad LWCO?0 -
Guage glass ....
If this is the same as the Dunkirk Plymouth, the guage glass is very long on the electronic cut off units and low water is about half way up the glass. Check the actual probe level... it is very high.
Boilerpro0 -
Also check
that the pipes between the boiler and the gauge glass are clear. If they are not, you can get a false reading which confuses the situation.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements