New Boilers

Steve_33
Steve_33 Member Posts: 2
I recently replaced my boiler and it does not have a blow off valve. I called the installer and he said that newer boilers dont have them. So where the heck does the sediment go? Is this some way of guranteeing I call a tech out regularily to get the thing cleaned?

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    Is this

    a steam boiler?
    Retired and loving it.
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    Is this a steam boiler?

    or a hot water boiler...do you mean a pressure relief valve? I am guessing you are refering to a low water cutoff...and a blowdown proceedure...some of the newer set ups use a probe type set up which means you don't need the weekly blowdowns...the probe should be checked at least on a yearly basis for sediment...kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Steve_33
    Steve_33 Member Posts: 2


    Yeah, steam boiler. This probe setup sounds like what I got. Not needing a weekly blowoff sounded too good to be true! I think now Ill invest in the auto fill so I can limit my basement visits. Granted, Ill probably go down and check things out on a monthly basis to make sure things are not out of wack.
  • joe_14
    joe_14 Member Posts: 138
    auto feeder

    steve be carefull a auto feeder will not maintain a proper operating level. what it provides is a safe minimum water level. a auto feeder is a saftey device not an operating device. you still should check your boiler water level regularly.


    joeg.
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Joe is right on


    If the hartford loop was installed for the "normal" operating water line, the probe LWCO may allow the boiler to run with a water line below the hartford loop. That can bring on what I call the "Big Ben syndrome".

    Clanging and banging where there was none before.

    LWCO's are safety devices and "auto-feeders" are too.

    You still need to monitor the system.

    Mark H