steam coil
cool
Member Posts: 3
i saw an air curtain that had a steam coil, the unit was installed about 6 ft below supply and the return line, so how is this thing working, condensate traveling up?
0
Comments
-
air curtain
pressure is pressure 2.3 ft. per pound for water 6feet 3 pounds of steam 6.9feet water will rise right up to the condensate return line0