Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

steam ??

tim smith_2
tim smith_2 Member Posts: 184
Hey all, got a question regarding end of main vent, have a long main, appx 600ft to end, at the end there was a small 3/4 trap, changed this to f&t trap, this is at the very end of system. I would also think it may be a good idea to put a Gordon #2 or Hoffman #? vent at this point also. Right now the only thing that will get the steam to move is the F&T at this point and I wonder if this will be fast enough venting to the return. Any comments appreciated. Thanks Tim.

Comments

  • The F&T should be plenty

    Steam in the returns can hold it closed, though, and would do the same thing to an air vent. Check for 200° return piping.

    Are there any water loop seals in the return piping that would prevent air from moving through them to get to the vent?

    Noel
This discussion has been closed.