Traps for 2 pipe steam-Broomell
Jim_45
Member Posts: 13
I have a 2 pipe Broomell steam system that had 2 of the original rads replaced years ago. There are two Burnham baserays (one about 4 foot, and one about 2 foot) that don't seem to have any traps. It was piped with 3/4" copper and the returns (and main dry returns near by) really heat up. I am sure steam is getting into the main dry returns thru these. Can I add traps on the individual returns before they empty into the common main return (There is not much room up by the baseboards)? If so, what type and size? I contacted Burnham but have not gotten a reply.
0
Comments
-
Yes, you can use traps
These will stop the steam from getting into the dry return. Hoffman (17C), Barnes & Jones (122) and Tunstall all make very good traps. Also make sure the dry return is well vented- Gorton's #2 vent works well on this type of system.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks
I tried to get the Gortons for the dry main vent but ended up with a Hoffman 75. It hisses so I plan on adding a second.0 -
Call Gorton
at 908-276-1323. Talk to Ken Kunz and tell him I sent you. He'll fix you up.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements