1 st System 200

Jamie_6
Jamie_6 Member Posts: 710
Not a bad little boiler! Went together well and the longest part of the job was installing the radiant in the kitchen!

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Mark Wolff
    Mark Wolff Member Posts: 256
    System 2000

    Nice job. Two things I noticed though, the Amtrol Extrol 30 expansion tank has to be oriented vertically with the threads at the top. This is to prevent dry rotting of the diaghram inside the tank. I have seen several of these prematurely rupture due to improper installation, so be careful of that.

    Also, boilers are required to have individual shutoff valves for the supply and return piping, seperate from the zone isolation valves. IMC 2000 1005.1