MAX BTU's
DennisDe
Member Posts: 16
What is the maxium BTU that can flow thru a 5" flue. I have been told that approx. 200btu can be handled by this flue size. Please advise max number
Depends on height
a 6 foot height chimney will handle 116,000 btu's and a 50 foot height will handle 210,000 btu's ( Nat Fuel Gas Code!)
diffterent amounts in between. Btu's / hour input.0 -
MAX BTU'S
30FT ON CHIMNEY0 -
Venting
Don't forget to consider the appliance you're dealing with, since there are different vent categories.
For instance, from the tables in the National Fuel Gas Code: A 5-inch b-vent, 30-feet high (no horizontal offset) can handle up to 220,000Btu/hr from a natural draft category 1 gas-fired appliance. But, that same 5-inch b-vent, 30-feet high (no horizontal offset) can handle up to 374,000Btu/hr from a fan-assisted category 1 gas-fired appliance.
If the 5-inch vent is being used for more than one appliance, the maximum changes.
If the appliance is not a category 1 appliance, then you need to consult the installation manual of the unit that you're venting.0 -
Depends
We need to know if the "lfue" you mention is the common vent ( what goes throught the roof) and what height and if your's is a fan assist or a nat draft.0 -
Not an easy question to answer
there are a lot of things to consider, most of which the others who have posted already have addressed.
I have a manual available titled "Natural Draft Venting Systems and Chimneys" it is strictly covering Category I Natural Draft Systems. If you are interested e-mail me.0
- 87.4K THE MAIN WALL
- 121 Chimneys & Flues
- 15.8K Strictly Steam