replacement gas valve

John Kirchner
Member Posts: 2
I have a lennox model #G12D282-6 natural gas furnace. (82000btu)
It has a Johnson Control G60QHL-1 pilot control mounted on top of the gas valve.
I have determined that the main gas valve is not opening.
the pilot and main gas valve solenoid coils ohm out ok.
I have checked operation sequence and have power to the main solenoid but it will not open.
Is there a replacement available for this and/or is there a retrofit valve I can use.
thank you,
J Kirchner
It has a Johnson Control G60QHL-1 pilot control mounted on top of the gas valve.
I have determined that the main gas valve is not opening.
the pilot and main gas valve solenoid coils ohm out ok.
I have checked operation sequence and have power to the main solenoid but it will not open.
Is there a replacement available for this and/or is there a retrofit valve I can use.
thank you,
J Kirchner
0
Comments
-
Replacement is
G600 LX-1 or you can replace just the valve with a VLV 49A-600R. This will allow you to keep the same configuration you have on the job.
Alternatives would be A Honeywell VR8345 Universal Gas Valve with a S8610U Universal Module replacement. I am pretty sure going with the same Johnson system will be cheaper and easier to install and rewire.0 -
Before you replace any parts,
Get the heat exchanger thoroughly inspected for cracks. I work on these G12 units all the time, and am constantly finding them with failed heat exchangers. If your HX is still sound, then I personally would install a Honeywell Y8600 spark ignition kit, which comes with a new ignition control, gas valve, and wire harness for easy hookup. Otherwise, to save yourself some money, I would replace the spark ignition with a standing pilot gas valve, which is easy to do since the flame sensor on the pilot can be removed and a standard thermocuple screwed in it's place. I personally would stay away from the Johnson controls, as I have had numerous problems with their ignition modules failing.
Just my 2¢ worth,
Glenn0
This discussion has been closed.
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 966 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements