chattering 8184g 4009
joe_14
Member Posts: 138
hi guys; one of my guys changed out an 8184g 4009 relay on a miller cmf 80 furnace, this is the second control in two days. the contol chatters for a couple of seconds then pulls in. check voltage 115v. checked for loose grounds found none.the furnace is 10 years old never had any problems like this. even tried feeding furnace off other leg in panel same problem. any suggestions will be welcomed. i wonder if burner motor could be the culprit.
thanks joe.g
thanks joe.g
0
Comments
-
I'd be looking.....
For stray light affecting the cadcell eye, and also check the stopped and running resistance of it. It should be very high when no light is present and somewhere around 800 or lower ohms when running. Chris0 -
Low voltage
I agree with cad cell idea.. Also maybe the low voltage is an issue. Extra resistance or a bad heat anticipator could be messing things up.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
8184G Chatter
Joe , Had the same thing happen to me ,and others, drove us nuts . What was happening on a call for hot water only the 8124A Aquastat was causing this problem , not the burner motor . Hope this helps with your diagnosis of the problem ,Al.0 -
thanks
thanks guys ill check these things in the a.m.0 -
Chattering relay
Joe oooops, Just re-read your post and my reply was for a hot-water system not a hot air system , was the relay a rebuilt or new ? if rebuilt try a new one after checking all other suggestions , Al.0 -
You should.........
check for proper polarity and good ground at panel. Also, how about the T-stat?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements