Boiler piping is perfect, but you should ramm that black magic marker down his throat. Sell him a $4000. car and write on the hood the date you sold it to him.

Comments

  • Frank_15
    Frank_15 Member Posts: 33


    I just had my steam boiler replaced this is what it looks like did the guy do it right
  • Frank_15
    Frank_15 Member Posts: 33
    and this is the first floor

    This is my tennants boiler. Is this one done right it's different from the other one
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    from what I see...

    looks piped well...I don't see any insulation...VERY important to have! kpc
  • Steamhead
    Steamhead Member Posts: 17,387
    Both look OK

    to me too. But Kevin is right about the insulation. And do those steam mains have vents at the ends?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Frank_15
    Frank_15 Member Posts: 33
    yes

    Yes there are 4 vents
  • Frank_15
    Frank_15 Member Posts: 33
    yes

    Yes there are 4 vents. 2 on each
  • Steamhead
    Steamhead Member Posts: 17,387
    2 vents on each main

    or one on each of 4 mains? To make sure they're right- how long is each steam main, and what pipe diameter? What vents are on each main now?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Frank_15
    Frank_15 Member Posts: 33


    1 on each of 4 mains. They are vent rite # 35. The longest main is no more than 15 ft'. All of the mains are 2".
  • bob young
    bob young Member Posts: 2,177


    whoever piped out these boilers is one damn good steamfitter.
  • I gotta agree with you

    He's done that before. I wish everybody's boiler were piped like that.

    Noel
  • Steamhead
    Steamhead Member Posts: 17,387
    Those vents might do OK

    on such short pipes. They are about the same size as a Hoffman #4A, which will vent about 0.4 cubic feet of air at 2 ounces pressure. That 15-foot pipe contains 0.345 cubic feet. If all mains fill with steam in about a minute (measured from the time the boiler starts making steam) you should be OK.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Frank_15
    Frank_15 Member Posts: 33
    thank you

    just wanted to make sure
  • Joe Gamble
    Joe Gamble Member Posts: 4
    Steam trouble

    I can not get my radiators to heat, I have replaced the traps. I know that I have an air problem, but I do not know where to install air vents. The trouble is on one side of the building, and I get air out of the steam side of the radiators when I open the union.
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    You might wnat to repost this as anew thread

    Things tend to get lost way down here.

    Boilerpro
  • Joe Gamble
    Joe Gamble Member Posts: 4
    Stream Trouble

    I can not get my radiators to heat, I have replaced the traps. I know that I have an air problem, but I do not know where to install air vents. The trouble is on one side of the building, and I get air out of the steam side of the radiators when I open the union.

  • Joe Gamble
    Joe Gamble Member Posts: 4
    Stream Trouble

    I can not get my radiators to heat, I have replaced the traps. I know that I have an air problem, but I do not know where to install air vents. The trouble is on one side of the building, and I get air out of the steam side of the radiators when I open the union.

  • Joe Gamble
    Joe Gamble Member Posts: 4
    Stream Trouble

    I can not get my radiators to heat, I have replaced the traps. I know that I have an air problem, but I do not know where to install air vents. The trouble is on one side of the building, and I get air out of the steam side of the radiators when I open the union.

  • Steamhead
    Steamhead Member Posts: 17,387
    There should be a vent on the dry return

    which is the return that runs overhead. If this vent goes bad, all the radiators feeding into that dry return will be cold.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • bob young
    bob young Member Posts: 2,177


    $4000 cars have no hoods!!!