Peerless Pinnacle Boilers
[Deleted User]
Posts: 0
I'm installing a new raidant floor system. The boiler that I'm using is the Peerless Pinnacle. I'm piping the boiler up with a primary - secondary Loop . The boiler Input is 140000- Net output is 112000. Do I size my primary circulator for the full load . How do I do this. Thanks for any help.
0
Comments
-
Pinnacle Boiler
I'm installing a new raidant floor system. The boiler that I'm using is the Peerless Pinnacle. I'm piping the boiler up with a primary - secondary Loop . The boiler Input is 140000- Net output is 112000. Do I size my primary circulator for the full load . How do I do this. Thanks for any help.0 -
Taco 0010
or equivalent for the 140.
Mark H
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Primary loop delta T
I notice that alot of the gas-fired condensing boilers have a high pressure drop through the heat exchanger, and the manufacturers supplying or recommending high head pumps. What temperature difference are you guys that install these looking for, and actually getting, in your primary loop on these systems (at the maximum input)? Thanks for any replies, in advance!0 -
Why is output so low?
I thought they were 92% those #'s say it is only 80%?
Ted0 -
Not Sure
where he got those numbers.
The Pinnacle is a Munchkin with green skin.
Mark H
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Fred, Do NOT use the info in the installation instructions provided by Peerless. Go to the Peerless website and then to the pinnacle page. On that page is a link? to download and print a nine page installation supplement that has the CORRECT piping and preesure drop curves. Select apump from there..Then call your wholesaler/rep and ask them why they did'nt tell you about that. I had a post on the wall 6 weeks ago about this and it was kicked out quickly.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements